I am installing a few different coloured strobes in a class 1 div 2 area. To me it looks like I will be required to eys each strobe before entering a jb. Is this correct? Strobes do not look to be factory sealed.
http://appliedstrobe.com/wp-content/uploads/2013/11/AST-14.pdf
Question 2
I am going from inside a structure to outside however the class and division are the same. On the exterior I will be connecting to a nema 4 enclosure using Myers hubs. Since the c and d are no different do I still require a boundry seal?
http://appliedstrobe.com/wp-content/uploads/2013/11/AST-14.pdf