B bcslc Member Location Salt Lake City, Utah Feb 27, 2018 #1 For the purposes of 110.26(E)(1)(a), would you consider a structural beam to be part of the structural ceiling, and therefore allowed to encroach into that space?
For the purposes of 110.26(E)(1)(a), would you consider a structural beam to be part of the structural ceiling, and therefore allowed to encroach into that space?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Feb 27, 2018 #2 IMO, yes.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Feb 27, 2018 #3 I agree.
kwired Electron manager Location NE Nebraska Occupation EC Feb 27, 2018 #4 Simple test here, remove beam, if structure collapses or partially collapses - it must have been structural. If structural member doesn't allow proper headroom that is another issue.
Simple test here, remove beam, if structure collapses or partially collapses - it must have been structural. If structural member doesn't allow proper headroom that is another issue.