Structural engineer built an IEEE 80 grounding grid calculator: looking for feedback

Location
Georgia
Occupation
Structural Engineer
Hey all, I'm a structural engineer who occasionally works on substation design. My day job is foundations and steel, but I've always been curious about the grounding side of the projects I work on, so I built an IEEE 80 touch/step voltage calculator at grid.fastercalc.com.

It has two analysis paths: the standard closed-form procedure (Km, Ks, Ki, Laurent-Niemann Rg, the whole Section 16 workflow) and a Boundary Element Method solver that discretizes the grid conductors, assembles the half-space Green's function matrix, and solves for the actual current distribution along the grid. The BEM gives you a spatial touch voltage map instead of just a single worst-case Em, and handles two-layer soil, custom rod placement, and fence transfer potentials. You can export PDF reports with all the intermediate calcs, and in BEM mode you get touch/step voltage heat maps with contour lines.

Results track well against the IEEE 80 Section 16 worked example, and BEM Rg lands within a few percent of the closed-form value. But I'm not an EE, and I know enough to know that's a problem. I'd really appreciate feedback from people who actually do this work:

- Does the methodology look sound, or am I misapplying something?
- For anyone who's done fall-of-potential testing — how close does calculated Rg typically get to measured?
- Any conditions where the closed-form assumptions really break down?

Happy to hear "you got this wrong" — that's the whole point of posting. Thanks in advance.
 
In 50 years of power systems engineering I have used IEEE 80 only once.
There are very few NEC installations that require this level of ground grid, open air utility style substations are the exception.
 
That's pretty neat! We do it all of the time here. I only learned about the actual means of calculation as an aside and couldn't help but feel like it would be fun.
In 50 years of power systems engineering I have used IEEE 80 only once.
There are very few NEC installations that require this level of ground grid, open air utility style substations are the exception.
 