Structural Member through a j box/pull box---- repost with pictures now

Status
Not open for further replies.
I need assistance in locating a code reference dealing with a contractor building a junction box in place with a structural beam running through the interior and no metal on the side against the concrete ceiling with penetrations through the concrete to an enclosure above? The uni-strut frame will hold the skin of the box. Also doesn?t such an enclosure require being listed?


P2290003.jpgJ box2.jpgj box7.jpgj box3.jpgj box5.jpg
 
If you call this a junction or pull box I have a hard time finding acceptance in 314.

If you want to call this an aux gutter the only thing in 366 that requires listing is nonmetallic gutters installed outdoors.

I do question whether or not there should be a back to this enclosure. Also consider that enclosures that stand on floor often do not have a bottom, but they are likely listed for that purpose.
 
The reason for posting it again

The reason for posting it again

I reposted this becuase I now have pics to load and no one has addressed my biggest concern. There is a structural beam in the so called enclosure.
 
I reposted this becuase I now have pics to load and no one has addressed my biggest concern. There is a structural beam in the so called enclosure.

If the structural member were wood or other combustible material there would probably be no question, which leaves the question being does there need to be a back to this enclosure? Large switchgear often has open bottom, is that any different other than that gear has been tested and listed? That gear likely can not be installed on a combustible floor.
 
I need assistance in locating a code reference dealing with a contractor building a junction box in place with a structural beam running through the interior and no metal on the side against the concrete ceiling with penetrations through the concrete to an enclosure above? The uni-strut frame will hold the skin of the box. Also doesn’t such an enclosure require being listed?


View attachment 6551View attachment 6552View attachment 6553View attachment 6555View attachment 6556

...read last sentence of 300.10 in '08 code
 
It is possible to comply with that without fully enclosing the back side of the assembly.

would he have an issue if the box above the floor is a junction box or a switch gear with bottom? Also has to be 'specifically permitted elsewhere in the code'
 
Last edited:
would he have an issue if the box above the floor is a junction box or a switch gear with bottom? Also has to be 'specifically permitted elsewhere in the code'
And that elsewhere may be 110.3(B), if it is listed and instructions allow open bottom entry.

This on site fabricated enclosure is probably not listed though.
 
And that elsewhere may be 110.3(B), if it is listed and instructions allow open bottom entry.

This on site fabricated enclosure is probably not listed though.

What is this listing you speak of?
Where is it required for a custom box?
 