Stub Thru

Status
Not open for further replies.

johnintexas

New member
We install Cat5 and coax cable for DAS (distrubited antenna systems) for cellular phone usage in existing buildings. Our equipment is usually installed in phone closets or IDF rooms that we put EMT stub-thrus above ceiling to be able to leave that room with our cable. Is there any code that covers fill of a stub-thru or is it not even considered a conduit system since it is usually only one piece about a foot long?
 
Re: Stub Thru

If the length of the raceway is 24" or less, then you can fill up to 60% instead of 40%. (Note (4) to tables)
 