(2) Selection of Ampacity. Where more than one ampacity applies for a circuit, the lowest value shall be used.
Exception: The second lowest value shall be permitted to be used provided the lowest-value portion length does not exceed 3.0 m (10 ft) or 10 percent of the adjacent portion(s) length, whichever is less.
Informational Note: See 110.14(C) for conductor temperature limitations due to termination provisions.
Statement of Problem and Substantiation for Public Input
Deleted 'given' and 'length' because they are unnecessary.
Changed the Exception wording to cover possibilities that would otherwise be excluded from a literally technical interpretation.
As an example, let's say we have a circuit 50' in length from panelboard branch circuit breaker to load terminals. The wires exit the panelboard enclosure through a conduit 4' in length containing 10 current-carrying conductors, are then routed 2' through a wireway with less than 30 current-carrying conductors, then continue in a conduit by themselves to the load.
The conductor ampacity for the portion exiting the panelboard in conduit would have the lowest value. The Exception can not be applied because the adjacent portion in the wireway is only 2' in length and there is no Code means to determine ampacity in an enclosure regardless of conductor length. Even if we could carry a higher ampacity across more than one adjacent portion, wireway to load is 44', and 10% past the transition at the wireway does not cover the 6' distance to the panelboard.
The circuit ampacity through the Exception, as reworded, is permitted to be that of the wireway or load-end portion of the circuit, whichever is less.