J jbolen Senior Member Jun 6, 2014 #1 This is common practice and I have done it myself many times but where would I find the article for the following. Rigid Stub ups with ground bushings under switchgear, transformers and generators the conduit doesn't terminated in the cabinet??
This is common practice and I have done it myself many times but where would I find the article for the following. Rigid Stub ups with ground bushings under switchgear, transformers and generators the conduit doesn't terminated in the cabinet??
iwire Moderator Staff member Location Massachusetts Jun 6, 2014 #2 Are you looking for the code section that requires bonding bushings? If so you will not find it, there are various requirements in the NEC that the choice of using a grounding bushing satisfies but it is a choice. You could bond the pipes another way and provide abrasion protection with other fittings.
Are you looking for the code section that requires bonding bushings? If so you will not find it, there are various requirements in the NEC that the choice of using a grounding bushing satisfies but it is a choice. You could bond the pipes another way and provide abrasion protection with other fittings.
J jbolen Senior Member Jun 6, 2014 #3 Conduit termination Conduit termination Looking for article that says I don't have to terminate conduit in a cabinet
Conduit termination Conduit termination Looking for article that says I don't have to terminate conduit in a cabinet
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Jun 6, 2014 #4 jbolen said: Looking for article that says I don't have to terminate conduit in a cabinet Click to expand... 300.12 Exception #2. Also note 408.5.
jbolen said: Looking for article that says I don't have to terminate conduit in a cabinet Click to expand... 300.12 Exception #2. Also note 408.5.
kwired Electron manager Location NE Nebraska Occupation EC Jun 7, 2014 #5 jbolen said: Looking for article that says I don't have to terminate conduit in a cabinet Click to expand... texie said: 300.12 Exception #2. Also note 408.5. Click to expand... Note it doesn't use the word terminate. The raceway still terminates at the equipment there is just exception of how to provide mechanical continuity.
jbolen said: Looking for article that says I don't have to terminate conduit in a cabinet Click to expand... texie said: 300.12 Exception #2. Also note 408.5. Click to expand... Note it doesn't use the word terminate. The raceway still terminates at the equipment there is just exception of how to provide mechanical continuity.