I never thought about this till today, or maybe I have & forgot.
Lets say you have a single or 3 phase service in a commericial application.
You have numerous conduit runs & MWBC's
CKT #1 is for EMRG lighting & #3 is for fixtures, they share a neutral in the same conduit. These ckts are phase A&B
Now in a different conduit you have CKT #1 for EMRG lighting & #7 is for outlets they share a neutral in the same but different conduit from the first example. These ckts are phase A&B
Are you allowed to do this? Sorry but I went brain dead today, fighting a sinus infection or summer cold
I think I can but not sure.
Sorry for the dumb question.