So I am doing this craft/trade show with my wife. I have a lot of down time. Its in a horse arena building. They roll carpet out. If the dirty wasnt so lumpy you wouldn't know the floors were dirt.
All the booths get temp power fed to them. OK its temp power, so not everything is 100% I get it. At first It seemed everything was safe, all the power taps in the spaces were GFI protected. But then I saw (picture name) Show 1.
The require you to state your watts needed when you sign up for the show, 500, 1000, or 1500. I guess this is not just for cost but to do a load calc maybe?
Well those fans look great. They stopped tripping after they started the "emergency breaker chilling"
Then "show 7"....That was in my wifes space. It's not extension cord its 10/2 NM. In a box on the floor. The box is bonded, but the supply is not GFI protected and the floor under that carpet is dirt.
Show 2: SER zip tied to a plastic fence.
Show 3: In use covers YEA! 50 amp receptacle exposed boo!
Show 4: Why not???
Show 5: SO cord zip tied to the tent. Its a bit sloppy.
Show 6: This was something a vendor did, its a NEMA 6 50P receptacle to an 20P adapter to a 3 way splitter.
All in all it was a good show, but I thought these were worth posting.
Show 4: Why not???