I have a situation with a 125A MLO load center fed out of a 100A breaker in a main distribution panel. The load center is located in a condo unit and feeds all of the circuits in the main condo unit and in an adjacent "lock-off" room. The lock-off room can be rented separately from the main condo unit, and the code official is requiring that it has its own load center.
I have found a sub-feed lug kit which can be installed in the main load center to feed another load center in the lock-off room. Since I am actually tapping the bus bars of the main panel (not tapping the conductors), does this installation fall under the tap rule 240.21(B)(1)? Also, does the sub-fed panel require a main circuit breaker, or can I make it MLO and comply with 408.36(A), Exception No. 1? Is there a section in the NEC that covers sub-feed and/or feed-thru lugs in panels?
I have found a sub-feed lug kit which can be installed in the main load center to feed another load center in the lock-off room. Since I am actually tapping the bus bars of the main panel (not tapping the conductors), does this installation fall under the tap rule 240.21(B)(1)? Also, does the sub-fed panel require a main circuit breaker, or can I make it MLO and comply with 408.36(A), Exception No. 1? Is there a section in the NEC that covers sub-feed and/or feed-thru lugs in panels?