Code reference, please?thecrazyezel said:I have heard about this configuration before. I do not believe it is legal because you are using the top panel as a raceway for the bottom panel and you are not allowed to use panels as a raceway.
thecrazyezel said:Please see this webpage
http://www.codebookcity.com/codearticles/nec/necarticle408.htm
Item 1 - To respect the modular integrity of the panelboard and not to use it as a raceway.
I agree with 408.3(A)(3).
if you choose to do the installation you could get called out on it by the AHJ.
iwire said:So do I, but that specific section only applies to sections of a switchboard.
A panel board does not have 'vertical sections"
I don't think so, I would point the AHJ to 312.8.
badcowboy said:.....As far as running conductors through one panel board for another, it is not allowed (2002 NEC 408.3(A)(3)). You may run wire horizontally if separated by a barrier, but not vertically unless that wire is intended for termination in that vertical section.