101010

Senior Member
My question is how far back in the code did seperating nuetral and grounds in sub panels come into affect? I'am asking this because recently I have seen quite a few comercial buildings that have 3 phase sub panels with only a nuetral. What happens if you do work in these panels ? Do you have to correct this?
 
101010 said:
My question is how far back in the code did seperating nuetral and grounds in sub panels come into affect? I'am asking this because recently I have seen quite a few comercial buildings that have 3 phase sub panels with only a nuetral. What happens if you do work in these panels ? Do you have to correct this?

Are you saying that these old panels are not supplied by conductors in metal conduit ?

David
 
they ran ser with the bare wire as the nuetral. The other 3 leg for the 3 phase. Just wondering if this was ever legal I dont now how long ago this was done.
 
101010 said:
they ran ser with the bare wire as the nuetral. The other 3 leg for the 3 phase. Just wondering if this was ever legal I dont now how long ago this was done.



you mean the bare wire for neutral ??


the last time i did see simuiar set up expect they used the bare exteral wire for grounding.

i dont really recalled to see if it was allowed per NEC but maybe it did many years ago but in European verison if this was same way it will be not allowed at all .


Merci , Marc
 
I didnt think that was ever legal in the code due to the CCC not being insulated because if the SER had a slice in the jacket you have the potential of getting wacked with the unbalanced load finding the shortest path. I see it a safety hazard and would recommend to change it, IMO.
 
101010,

Are the EGC and the neutrals all landed on the same bus, if not, is that bus

bonded to the metal of the panel? Regardless, I would inform the owners

of these properties of the danger and even offer to bring the EI in if they

need a second opinion.

It's like the doctor who passes by someone that needs help, or a fireman

who looks the other way, how else will this get fixed if we don't do some-

thing about it?? It will only get fixed after someone gets hurt or worst!
 
Dean83169 said:
I didnt think that was ever legal in the code due to the CCC not being insulated because if the SER had a slice in the jacket you have the potential of getting wacked with the unbalanced load finding the shortest path. I see it a safety hazard and would recommend to change it, IMO.

Dean, not that the situation in this thread is correct but, the uninsulated conductor in SE was used for many years as a CCC and still is in existing installations, see 250.140

Roger
 
I read the post, did you? Its bad enough that people come to this site to post questions but then to get so many answers and some wrong ones, its like you have to read through them all and take a general concensus of what everyone wrote because the code book has always been the problem of INTERPRETATION. I mean no disrespect Roger to you this is a general problem.
 
101010 said:
My question is how far back in the code did seperating nuetral and grounds in sub panels come into affect? I'am asking this because recently I have seen quite a few comercial buildings that have 3 phase sub panels with only a nuetral. What happens if you do work in these panels ? Do you have to correct this?

"What happens if you do work in these panels ? Do you have to correct this?"
As an inspector coming to this job there's 2 situations that I would look for:

1] If you have no interaction with this panel, the panel is beyond the scope of your work. . Your permit covers your scope of work and that's what your inspection report from me would cover. . Beyond the scope of work, I would contact the property owner if I saw any violations but I would recommend a withholding of occupancy to my CBO, Certified Building Official [who is the AHJ in Ohio] only if the violation was considered a serious hazard and danger. . This wouldn't affect your permit, your inspections, or your approvals.

2] If you did interact with this panel, you couldn?t get an approval to connect any new wiring to this panel. . The new circuiting does not have proper grounding when terminated in that panel. . You would need to fix the panel before you could use it to supply the installation under your permit.

David
 
Dean83169 said:
I read the post, did you? Its bad enough that people come to this site to post questions but then to get so many answers and some wrong ones, its like you have to read through them all and take a general concensus of what everyone wrote because the code book has always been the problem of INTERPRETATION. I mean no disrespect Roger to you this is a general problem.

Dean, speaking of reading, did you read the first eleven words in my post"

You made a statement that a you didn't think it was ever legal due to an uninsulated CCC, well that is not the case, it may be a different application but uninsulated CCC's have been and still are legal.

Would your concern of somebody getting "wacked" by touching it not be a concern in a range or dryer installation?

You also made a statement that the load takes the shortest path, where is this shortest path going to?

The truth is that the statement of "electricity takes the shortest path" is not completely true, it takes all available paths and will divide proportionately depending on the impedance of each individual path to the source.

In conclusion, if your worried about someone getting the wrong answer this would be a perfect example of it. An apprentice would read your blanket statement and if he/she ever happened upon an old dryer or range circuit there is a good chance they would have no clue that the strands in the sheath could be carrying current because they read on a forum that it couldn't be the case since it was (supposedly) never allowed.

Dean, don't get upset if someone replies back to your post with a correction or a detail clarification, it happens all the time and will continue to do so.


Roger
 
Dean83169 said:
I didnt think that was ever legal in the code due to the CCC not being insulated because if the SER had a slice in the jacket you have the potential of getting wacked with the unbalanced load finding the shortest path. I see it a safety hazard and would recommend to change it, IMO.

I agree with your statement, although it is the same situation as running SE cable on a house (I know this was a recent discussion and I'm not opening it up again). If the standard SE cable feeding a house were to get a slice in the outer jacket, the braided neutral would be exposed and it too will be carrying the imbalance between the 2 phases.
 