I read the post, did you? Its bad enough that people come to this site to post questions but then to get so many answers and some wrong ones, its like you have to read through them all and take a general concensus of what everyone wrote because the code book has always been the problem of INTERPRETATION. I mean no disrespect Roger to you this is a general problem.
Dean, speaking of reading, did you read the first eleven words in my post"
You made a statement that a you didn't think it was ever legal due to an uninsulated CCC, well that is not the case, it may be a different application but uninsulated CCC's have been and still are legal.
Would your concern of somebody getting "wacked" by touching it not be a concern in a range or dryer installation?
You also made a statement that the load takes the shortest path, where is this shortest path going to?
The truth is that the statement of "electricity takes the shortest path" is not completely true, it takes all available paths and will divide proportionately depending on the impedance of each individual path to the source.
In conclusion, if your worried about someone getting the wrong answer this would be a perfect example of it. An apprentice would read your blanket statement and if he/she ever happened upon an old dryer or range circuit there is a good chance they would have no clue that the strands in the sheath could be carrying current because they read on a forum that it couldn't be the case since it was (supposedly) never allowed.
Dean, don't get upset if someone replies back to your post with a correction or a detail clarification, it happens all the time and will continue to do so.