I don't see the AC unit load being included in the neutral calculation in Example D2(b).In D2b they added the AC units 10080va and used the number in the neutral contribution
I don't see the AC unit load being included in the neutral calculation in Example D2(b).In D2b they added the AC units 10080va and used the number in the neutral contribution
i totally agree with you from a safety standpoint that 120v loads on opposite phase will have cancelling affect, and 240v L-L loads should not be counted but cant find it in code or examples.Also it's not only L-L loads, equal 120 volt loads on each ungrounded conductor will cancel the neutral load. At 120 volts, 75 amps on each ungrounded conductor will yield a 0 amp neutral load
Upon further review see that. There has to be a code ref I'm missing on L-L loadsI don't see the AC unit load being included in the neutral calculation in Example D2(b).
Agreed and i would say as close to impossible as you can getIf you truly do not know what will be connected to this feeder, then you are correct. Perhaps the home owner will install a set of 120V bitcoin rigs, and then only operate half of them at a time.
Absent any other instructions, (for example the 70% demand reduction for ranges or electric dryers), then you need to do the article 220 calculation for the loads connected to the neutral. 220.61(B)2 gives a demand reduction factor for the neutral when the feeder is larger than 200A, but that demand factor doesn't apply.
The only reduction that you can apply on a 90A feeder to a garage is eliminating any loads not actually connected to the neutral. All you really have is the experience of the members here who say that it is very unlikely that any residential use of this 90A circuit won't have some significant L-L loads.
-Jon
It's 220.61(A).There has to be a code ref I'm missing on L-L loads
D2(b) is an Example of the L-L loads not being counted in the neutral calculation. Both the 240V Air conditioner load and 240V Water Heater (you have to make an assumption that it's 240V) are not included.240v L-L loads should not be counted but cant find it in code or examples.
The 220.61 neutral calculation assumes that the load is balanced on the phases. It's not for a worst-case situation where all of the loads are on one phase.Thats where i have been looking seems like only cooking units and dryers. I do know this should not be a problem, long as something is on both phases. I cant find anything on load balancing that would make it OK. The condition where i could see a safety issue is if someone purposely put all the load on one phase.
I wouldn't say that 220.61 directs you to assume that. I would say it references the actual division of the L-N loads between ungrounded conductors:The 220.61 neutral calculation assumes that the load is balanced on the phases.
I agree and that's why I commented earlier that would be up to the next guy to figure out not the installer of the feeder who may have no knowledge of the future loads.So if you go ahead and install them balanced, you can calculate it that way. If you install all L-N loads on one ungrounded leg, you are required to calculate it for that worst case.
Those are L-N-L loads with known-reduced neutral currents, not L-L-only loads.Thats where i have been looking seems like only cooking units and dryers.
Those are L-N-L loads with known-reduced neutral currents, not L-L-only loads.
Can you conceive having 90a of neutral current, even if you intentionally try to?
The electrician's responsible for balance-loading of L-N loads. Hey, that's you!
If you are saying that you have to assume that all the L-N loads in the entire panel are on one bus, leaving half of the space unused, I disagree. 220.61(A) means that you get to look at the exact division of of the L-N loads among the two or three busses, and just size the neutral for the most heavily loaded bus.IMHO if one were to only have L-N loads (say 120V receptacle circuits on a subpanel), code does not provide a way to do the calculation to reduce the neutral until the calculated load exceeds 200A. No matter how 'balanced' the installation is.
Exactly, which should (theoretically) not be much more than half (third for 3ph) of the feeder's calculated load.If you are saying that you have to assume that all the L-N loads in the entire panel are on one bus, leaving half of the space unused, I disagree. 220.61(A) means that you get to look at the exact division of of the L-N loads among the two or three busses, and just size the neutral for the most heavily loaded bus.
Yes, but at half of the voltage, so the same current.Exactly, which should (theoretically) not be much more than half (third for 3ph) of the feeder's calculated load.
If you are saying that you have to assume that all the L-N loads in the entire panel are on one bus, leaving half of the space unused, I disagree. 220.61(A) means that you get to look at the exact division of of the L-N loads among the two or three busses, and just size the neutral for the most heavily loaded bus.
I would think you need to do the load calculation before the installation, so you know what size conductors to install.So if you go ahead and install them balanced, you can calculate it that way. If you install all L-N loads on one ungrounded leg, you are required to calculate it for that worst case.
The two are intertwined.I would think you need to do the load calculation before the installation, so you know what size conductors to install.
Yes, I see that example D(1)(a) assumes the load is perfectly balanced--the neutral load is taken as all of the 120V load (after the 100%/35% computation), plus 70% of the 120/240V load (range/dryer), and then divided by 240V. Which is the same as taking half (perfectly balanced) and then dividing by 120V.In any event, there are several Annex D examples. They assume the load is balanced.