Yes.
In the US we run a bonding conductor (called the Equipment Grounding Conductor, EGC) that is separate from the grounded conductor (neutral) after the service disconnect(s). i.e. they are bonded together in the service disconnect(s) and thereafter kept separate on the load side. It has been required to run the separate EGC within the same structure since at least the 1950s, I believe.
The exception for detached structures before 2005 allowed the circuit to the detached structure to be treated the same as a service, i.e. bring only hots and neutral to the building, then ground the neutral and bond the EGCs at the first disconnect. That is no longer allowed except for existing situations that were installed compliant before 2005.