What if the disconnect is beside of another disconnect. In the case at my church, there's a 400 amp disconnect feeding another 400 amp disconnect right beside of it and the second 400 amp disconnect if feeding a 100 amp fuses disconnect right beside of that. The feeder in question is on the 100 amp disconnect beside of the other 400 amp disconnect. They are all bonded at each disconnect. I'm assuming all needed to n/g should have been connected together at the first 400 amp disconnect. This is a very old service to the church that was probably installed 100 years ago. Would there be objectionable current at the 3 disconnects grouped together if all 3 had n/g connected together in each disconnect?As long as the N-G bond is only in one place, there are no parallel paths to carry objectionable current.