The length of the feed-through conductors is 6'? Then you can use the 25' tap rule with a main CB in the sub-panel.50 feet - 6- ft max distance btwn main feed thru and sub
Why the disconnect when you could just run the #3/0 to the sub-panel?my solution - i think straight forward - forgive sloppy script
conductors in pvc are 1/0
i was sure that i an not connect 1/0 to bottom feed thru lugs on 200 A panel
thats how this started - someone pulled 1/0 from 125A sub panel to a 200A feed thru - and it looked not right to me.
they asked if they could use cb 100A i said yes - but the 1/0 are too large to fit Cb and there was no space for 2pole CB