If I add a sub panel fed by a 100A breaker, am I correct that I need to feed with #1 thwn copper feeders?  I am assuming 75 degree terminals and factoring in continuous load. 100 * 1.25 = 125A continuous load.  From 310.15(B)(16), #2 copper is good for 115A, so I need to go up to the next size, #1 good for 130A.  Am I correct here?
	
		
			
		
		
	
				
			
				