I need a reminder about sub panels in seperate buildings, what conditions require re-bonding the neutral to the ground?
I need a reminder about sub panels in seperate buildings, what conditions require re-bonding the neutral to the ground?![]()
yes but don't re-bond the grounded conductor.
yes but don't re-bond the grounded conductor.
Neutral remains isolated.
this would be considered an out building. I beleive the panel will need a main and need its own ground rods
The former. The OCPD is at the source end (unless the panel's rating is lower than the feeder and its OCPD.)What kind of main does it need. A main disconnect or a main OCPD.
What kind of main does it need. A main disconnect or a main OCPD. Don't you just hate the technical correctiveness of the code.
Rick
Just a disconnect unless the sub panel is further than 200' away because the short circuit current rating drops to 300 amps available instead of 500.
Can you please explain this sentence?
I understand what short circuit current is and the fact that you have a long circuit with a higher impedance would mean less available short circuit current available right?
What is the reference to 300amps and 500amps?
lil help please
add a bump ,i wanta know too.Bump. Hoping to get reply.
I need a reminder about sub panels in seperate buildings, what conditions require re-bonding the neutral to the ground?![]()
Per 2005 Code, for sub-panels.
Never "Re-Bond" the insulated Neutral. It is 'created' in the primary panel.
... this violation would send neutral current from the sub-panel
back down the EGC to the primary panel.