sub panel grounding

Status
Not open for further replies.
this would be considered an out building. I beleive the panel will need a main and need its own ground rods

What kind of main does it need. A main disconnect or a main OCPD. Don't you just hate the technical correctiveness of the code.
Rick
 
Just a disconnect unless the sub panel is further than 200' away because the short circuit current rating drops to 300 amps available instead of 500.

Can you please explain this sentence?

I understand what short circuit current is and the fact that you have a long circuit with a higher impedance would mean less available short circuit current available right?

What is the reference to 300amps and 500amps?

lil help please
 
I need a reminder about sub panels in seperate buildings, what conditions require re-bonding the neutral to the ground?:confused:

Per 2005 Code, for sub-panels.

Never "Re-Bond" the insulated Neutral. It is 'created' in the primary panel.
... this violation would send neutral current from the sub-panel
back down the EGC to the primary panel.

Always Bond the EGC, the un-insulated ground wire from the primary panel.
... this is the return path for equipment faults to ground.

Always use a Ground Rod.
... for lightning/HV shunt to earth reference ground.

Can use a Back-Fed CB for the Main.

And never hammer your staples onto the Romex,
it can setup a condition called 'pyroformic-carbonization'.
I think this term can be found in the NEC Handbook, '05.

I can give you a money back guarantee
this advice is from NEC. :smile:
 
Per 2005 Code, for sub-panels.

Never "Re-Bond" the insulated Neutral. It is 'created' in the primary panel.
... this violation would send neutral current from the sub-panel
back down the EGC to the primary panel.


Glen, you are correct that it could not be re-bonded to an EGC however, a neutral to an out building can be regrounded per the 2005 and earlier NEC if the installation is installed per 250.32.

Roger
 