Dennis Alwon said:Well, I guess I have been lucky because I know I have installed panels on the walls in the garage common to the living areas.
That is a problem if the wall needs a 2 hour rating.
Dennis Alwon said:Well, I guess I have been lucky because I know I have installed panels on the walls in the garage common to the living areas.
iwire said:That is a problem if the wall needs a 2 hour rating.
Dennis Alwon said:Correct but for a residence I always thought it was a one hour rating. I may be wrong--- I hate saying that.
Dennis Alwon said:Correct but for a residence I always thought it was a one hour rating. I may be wrong--- I hate saying that.
stickboy1375 said:I've never seen more than 5/8 rock installed on the garage side with living space on the other side of the wall...
Dennis Alwon said:I am not sure why a metal can would kill the firewall rating but it may.
Quote:
Originally Posted by Dennis Alwon
Well, I guess I have been lucky because I know I have installed panels on the walls in the garage common to the living areas.
Iwire said:That is a problem if the wall needs a 2 hour rating
M. D. said:Don't you mean if it were IN the wall and not on the wall ???
Cavie said::-? You guys are over thinking again. Do you not put plastic outlet boxes in these garage walls?????? Panels in garage walls that are next to living areas are acceptible.
bobrenwick said:OK, it?s coming back to me why we "normally" do not put panels in the attached garage. The fire wall issues. I'll see what I can find out about their code in Touqerville, Utah.
R309.2 Separation required. The garage shall be separated
from the residence and its attic area by not less than 1/2-inch (12.7
mm) gypsum board applied to the garage side. Garages beneath
habitable rooms shall be separated from all habitable rooms
above by not less than 5/8-inch (15.9 mm) Type X gypsum board
or equivalent. Where the separation is a floor-ceiling assembly,
the structure supporting the separation shall also be protected by
not less than 1/2-inch (12.7 mm) gypsum board or equivalent.
Cavie said::-? You guys are over thinking again. Do you not put plastic outlet boxes in these garage walls?????? Panels in garage walls that are next to living areas are acceptible.
raider1 said:Here is what that section says:
There is no real "fire rating" of this wall, just the requirement for a layer of 1/2" sheetrock or equivalent. You will need to check with the local building department to see what they have determined is the equivalent of 1/2" sheetrock. There are places that will accept the metal panel box and the cover as equivalent of 1/2" sheetrock.
Chris
Dennis Alwon said:So what does equivalent mean--- does it mean equivalent in fire rating???? How do you equate sheetrock to anything else--- Luan?, plywood? I assume it means in fire rating but that is not there in words.
lpelectric said:Type "X" means fire-rated.
eprice said:Not quite. Assemblies are fire rated, individual components are not. For a particular wall assembly to be fire rated, for example, it would need to be tested as built. Most fire rated assemblies use type "X" sheetrock, but a piece of type "X" sheetrock by itself doesn't cary a fire rating. Type "X" just means that it is designed to perform better under fire conditions. The main difference that I am aware of is that there are fibers in the gypsum to give it more strength after a fire burns the paper face off.
The quote above from the IRC doesn't call for any particular fire rating. It does require type "X" sheetrock on the ceiling in certain circumstances, but it does not require type "X" sheetrock on walls.