Need little support here...
I will be installing a 125 amp 16 space panel in a garden apartment. 120/240 single phase
main lug......... I'll be feeding it with #6........... problem is .... the main lugs are rated #4 awg min.
There's and area above the panel.
1- Splice 6's to 4's
2- replace the one hole lugs to smaller lugs
3- do they make a wire connector from 6 to 4
try to locate a 60 amp panel with 16 spaces..... (not having much luck)
100 amp panels are also #4 min
suggestions??
Thank you