OK I have one... what if the sub panel is lugged off the main bus of a larger panel next to it or tapped off a larger set of feeders... the wires and smaller bus still need overcurrent protection. :D
 
Last edited:
Stew, as was mentioned in the first post a sub panel does not require MBR if its in the same building as the panel feeding it, (provided it is not lugged off the bus of that panel or tapped off a larger set of feeders as either case would create a need for OCP) ;)

Sorry if everyone got a little carried away but I guess they thought you were asking a quiz question. :D
 
Last edited:
So then in a detached building, such as a detached garage, the panel must have a main breaker installed? Does the 6 switch rule apply here, or is a subpanel of any size required to have the main breaker?
 
racerdave3 said:
So then in a detached building, such as a detached garage, the panel must have a main breaker installed? Does the 6 switch rule apply here, or is a subpanel of any size required to have the main breaker?
If you don't have a seperate disconnect then yes MBR or 6 switch rule applies. The bigger challenges come in grounding and bonding.
 
electrofelon said:
I believe in this case th #2 SER will need a 90 amp ocpd unless your jurisdiction allows 310.15(B)(6)n to be applied to all feeders.
Correctamundo! I learned that the hard way: 90a breakers aren't cheap!
 