sub panel or not

Status
Not open for further replies.

jbhindes

Member
I installed a 200 amp meter base and feed through panel on the exterior of a residential building and ran 4/0 ser to a 200 amp interior panel. Do I need to separate my neutral and grounds in the interior panel? I ran my #4 water pipe and my #6 ground rod grounds into the feed through panel.
 
Re: sub panel or not

Your interior panel is a sub panel fed from your exterior Meter/Main panel, yes you must seperate your grounds and neutrals in all panels after the exterior panel.

Dave
 
Re: sub panel or not

Well, there is no OCPD distinguishing this as a seperate feeder. It could be argued these conductors are just some long buss extensions, especially if they are in metalic conduit or tubing. ;)

Roger
 
Re: sub panel or not

200 amp meter base and feed through panel
What is a feed through panel? Does it have a Main CB? And if you ran SER cable why would you even think about connecting the grounded and grounding conductors together at the panel?

[ April 24, 2005, 08:49 PM: Message edited by: infinity ]
 
Re: sub panel or not

A combination meter/main feed through panel has a meter socket, a main breaker that feeds a few circuit breaker spaces and also Lugs at the bottom which are what you use to feed the indoor panel. The Main breaker in the "feed through" panel is the point of disconnect therefore requiring all neutrals and grounds to be seperate after that point. SER is fine, just remove the bonding screw and keep the two seperate.
;)
Dave
 
Re: sub panel or not

Frank, the first sentence adds:

"...Except at the point of load terminations..."

Aren't the feed through lugs located at a point of load terminations?

Honestly, I'm not sure what that means!?!
:confused:

Dave
 
Re: sub panel or not

Originally posted by roger:
Well, there is no OCPD distinguishing this as a seperate feeder. It could be argued these conductors are just some long buss extensions, especially if they are in metalic conduit or tubing. :D
 
Re: sub panel or not

Paul, forget the inspector and tell us in your opinion why could'nt this be the case.

Roger
 
Re: sub panel or not

I concur with Roger's statement here - please tell us in your opinion why couldn't this be the case.

Although the "Root Reason" behind what Roger posted in his last reply is known by myself and several others (a past thread brought up extreme "out of the box" thinking), I have a feeling the "Laughter" may be inverted in this case.

Not trying to start any trouble, just kind of on the same Hz as Roger.

Scott
 
Re: sub panel or not

Hello Scott, we will see where it goes this time.

Roger
 
Re: sub panel or not

Wouldn't this "extended buss" have to be listed for the purpose?

Field designed and assembled, listed?

Edit: Edited :D

[ April 25, 2005, 07:39 PM: Message edited by: physis ]
 
Re: sub panel or not

Sam, the NEC doesn't require a listing for Panels or the Busses, so we can leave that here.

As an aside, only HID and SW designated breakers are specifically required to be listed. see 240

Roger
 
Re: sub panel or not

Now you got me wondering,instead of panel being in the house,how would you classify it if you nippled the panel next to the feed-thru outside. would it still be the service equipment,or a sub?

frank
 
Re: sub panel or not

Alright, I know you're no slouch Rog. And I'm sure you've looked at this rather closely (you have brought it up before). But I will find where it doesn't work. :cool:

How bout 408.3(C) "Each switchboard or panelboard used as service equipment, shall be provided with a "main bonding jumper"".

250.28 "main bonding jumper shall be used to connect the equipment grounding conductor(s) and the service disconnect enclosure".

Not "service disconnect(s) enclosure(s)".

Can we have two main bonding jumpers?
 
Re: sub panel or not

Sam, with the metalic raceways considered, why do we have "enclosures", (plural) in effect it is one.

Think of a buss duct with a service main at one end and 60' (or 160' if you want) away a set of branch circuit breakers as an integral unit within this duct assembly.

Why would this be different?

Roger
 