brian john
Senior Member
- Location
- Leesburg, VA
Re: Sub panel question
eprice:
In the "legal" system the only time there is current flow on the EGC (other that leakage current) is when there is a short/fault downstream from the grounded conductor/neutral. If the person or bodies you mentioned happen to inadvertently become this path the downstream voltage is typically too low to have a shocking impact on the inadvertent human conductor.
eprice:
In the "legal" system the only time there is current flow on the EGC (other that leakage current) is when there is a short/fault downstream from the grounded conductor/neutral. If the person or bodies you mentioned happen to inadvertently become this path the downstream voltage is typically too low to have a shocking impact on the inadvertent human conductor.