In a dwelling I believe a #2AL feed to a sub panel needs to be protected by a 90 amp breaker max after a 200 amp main breaker panel. I also believe if the main breaker panel is supplied by a #2 and protected by a 100 amp breaker then a sub panel feed from this with #2AL can also be protected by a 100 amp breaker, I cite 215.2 (A) (3). opinions if this is correct, Thanks.