I know this has been asked multiple times but I'm wondering why we can calculate the back-up heat at 65 percent if doing a load calculation for a house but if that same heat is coming from a sub-panel, it has to be calculated at 100 percent? I'm getting ready to install a sub-panel for an addition over a garage and wondering if everything has to be calculated at 100 percent?
It will have a dryer, water heater, washer, a 1.5 ton mini-split for the garage and I believe a 2 ton heatpump with 7.5 kw of back-up heat. If this same scenario was a "whole house" it would have some demand factors involved. I know you loose the diversity factor with a sub-panel and I know the total load calculation comes from the entire dwelling but just trying see what I need for the sub-panel feeder. I haven't checked the nameplate on the heatpump and mini-split yet, but will before choosing the feeder for the sub-panel.
It will have a dryer, water heater, washer, a 1.5 ton mini-split for the garage and I believe a 2 ton heatpump with 7.5 kw of back-up heat. If this same scenario was a "whole house" it would have some demand factors involved. I know you loose the diversity factor with a sub-panel and I know the total load calculation comes from the entire dwelling but just trying see what I need for the sub-panel feeder. I haven't checked the nameplate on the heatpump and mini-split yet, but will before choosing the feeder for the sub-panel.