Re: Sub-Panel?
You are right Bennie, sub-panels do not exist. If you look at my posts, I normally use the term distribution panelboard or downstream panelboard.
Now to address your comment, in the old days, we didn't run a separate grounding conductor. The "tail panels" were connected directly to the main bus and the tap was run to it without anything to ground it but the neutral. Essentially, it was part of the main service equipment.
That was then, this is now. You are now required to keep the grounding conductors separate from the grounded conductors. You can't reground the neutral after you leave the service equipment. Therefore, the downstream panelboarrds are just another piece of equipment that must be grounded like any other piece of equipment.
Now a question for you. Why does the Code need to define a downstream panelboard?