Sorry Charlie: I didn't answer your question.
In my opinion and my interpretation of the NEC and the evolution of new methods, I feel the absence of a definition of a sub panel is due to the definition being the panels are all service panels, and can be connected accordingly.
The only requirement is to prevent objectionable current flow by observing 250.6 in its entirety.
3 wire cable does not present multiple ground points, so separation of ground and neutral conductors are not necessary.
When 4 wires are used the ground/neutral separation must be made to eliminate one of the ground paths.