Re: sub panels

If the sub panel is in the same building as the service panel that feeds it there is no requirement to have a main in a sub panel. This assumes the feeder has a rating the same or less than the sub panel.

If the sub panel is in a separate structure there is still no requirement for a main breaker again assuming the feeder has a rating the same or less than the sub panel.

However there is a requirement for a disconnecting means in a separate structure. Often the easiest way to comply with this is a main breaker panel.

Bob

[ September 16, 2004, 05:35 PM: Message edited by: iwire ]
 
Re: sub panels

Originally posted by tjhelectric: main breaker or not?
I don?t understand the question.
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Are you asking if a main breaker is required under any specific circumstances?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Are you asking if a main breaker is preferred (i.e., design choice) under any specific circumstances?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Are you asking if any of us have good reason for using, or not using a main breaker under any specific circumstances?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Are you asking for the code section that discusses main breakers?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Are you asking if any of us have a main breaker for sale? ;)</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
 
Re: sub panels

LOL @ charlie b

After several minutes, I'm still laughing at the for sale comment. :D
 
Re: sub panels

ok iwire,
I get the feeling you're just trying to stir the pot here :) . What have you got up your sleeve? It would be the easiest way to satisfy 240.21(C)(6)(2) for example, wouldn't it?
 
Re: sub panels

Originally posted by eprice:
ok iwire,
I get the feeling you're just trying to stir the pot here :)
No way, not me :)

It may be the easiest way to meet certain code requirements but that is a design issue as they say. ;)
 
Re: sub panels

Well, in case tjhelectric doesn't reply, I'll ask.

Are you asking if a main breaker is required under any specific circumstances? Yes

Are you asking if a main breaker is preferred (i.e., design choice) under any specific circumstances? Yes

Are you asking if any of us have good reason for using, or not using a main breaker under any specific circumstances? Yes

Are you asking for the code section that discusses main breakers? Yes

Are you asking if any of us have a main breaker for sale? What you got? :)

Brentp
 
Re: sub panels

Originally posted by iwire:

I do not believe that there is a single instance in the NEC that requires us to use a main breaker panel. :)

It may be the easiest way to meet certain code requirements but that is a design issue as they say. :) And I may have to agree with you, But I'm gonna think on it for a bit first. :)
 
Re: sub panels

Trolling for inspectors :D what an idea
 