jwelectric said:
I am always trying to learn so based on your statement the equipment grounding conductor serves no purpose at all and we can use the grounded (neutral) in place of the equipment grounding conductor.
Also based on your comment should the equipment grounding conductor and the grounded (neutral) be bonded together on the load side of the service in branch circuits and feeders where the conductors are less than a 1/0 then there would be no violation of 310.4?
If there is not ONE IOTTA of hazard in the bonding of the two in a branch circuit then it would be alright to just jump from the grounding terminal of a three wire receptacle to the grounded (neutral) terminal in order to have a fault path for the receptacle.
Please help me to understand this. Am I correct in my understanding of what you are saying?
What I said is that bonding the neutral to the EGC at the main AND the subpanel does not change the level of hazard.
Should we choose not to employ a separate EGC then we would need to bond the Grounded conductor to the casing at every single location. The danger here is that if the neutral is open the case would be at line voltage compared to the ground. To avoid that you would need to have a bonding connection to ground at every location where you have connected the grounded conductor to the enclosure.
Purpose of the grounding path, weather it is a separate groudning conductor or the conduit, is to provide a relaively low impedance fault current path in case the ungrounded conductor inadvertently came into contact with non-energized conductive parts of the electrical apparatus. Should the grounded conductor (neutral) accidentaly contact to the same parts since the case is already grounded via the EGC and the grounded conductor is bonded at the service origin.
In case of a ground fault close to the equipment the fault current would take the following paths:
a - Fault to case
b - case to EGC,
c - Case to earth(1),
d - EGC to grounded conductor in the subpanel,(2)
e - (2) subpanel grounded and EGC will proportionately split the current between them,
f - both EGC and grounded conductor(neutral) carries the fault current back to the WYE point of the source to comnplete the fault circuit,
g - (1) there will be a high impedance component of the fault current that will flow though the earth - however good the incidental or intentional grounding of the equipment case at the use point - back to the WYE point of the source.
All these parallel and series paths will complete the circuit, but the flow of the current only goes through one protective device on the ungrounded conmductor of the circuit. The additional parallel paths on the grounded side reduce the overall total impedance of the circuit when comnpared to the pre-fault segment of the wiring so that the fault can open the breaker.
Should there be loose grounding connections or corroded or long conduit path providing high impedance path to complete the circuit it is possible that the fault current will remain insufficient to open the protective device.
In addition, if the equipment casing itself does not have a ground connection at it's location and somehow its mounting is insulated, it is possible to have line voltage on that device's casing. In that case if one is to touch the device casing and another item that is effectively grounded, such as a waterpipe, a gas-line or a metallic structure that is grounded throught connections to the foundation a "shocking" experience is to be expected. ;-) If the case is connected to the surrounding grounded structure, even if the impedance path back to the source ground bonding point is to high to operate the protective device there is no potential difference between the equipment and its surroundings therefore no electrocution danger is present. We can talk about step voltages, but again in low voltage sitiations - under 1000V - it is insignificant.
The tricky thing about EGC's and grounding connections is that they are "passive" connections, eg. they do not normally carry currents - not quite true, but insignificant to the argument - so you only discover their defects when you need them!