don_resqcapt19 said:Lazlo,
It is based on the percent of the total resistance around a 5/8" x 10' ground rod as shown in Chaper 4, Table 9 of the 1991 IEEE Green book. That table shows ~86% of the total resistance within 5' of the ground rod (yes, I said 3' but that was from memory without checking). That would mean if you connect a 10' ground rod to a 120 volt source and touched the source and the earth 5' away from the rod you would receive a 103 volt shock.
Other than lightning protection and possibly votlage stablaziation, there is no reason to connect the system to earth. It does not increase the safety of the system in any way.
They can be a problem on low voltage systems that do not have a code compliant fault clearing path. One example is where a metal parking lot light pole is installed with only a grounding electrode and not the code required equipment grounding conductor. If there is a line to pole fault anyone one touching the pole and the earth 3' away from the pole will receive ~81 volt shock, assuming a 120 volt supply. (Table 9 shows ~68% of the resistance at 3')
Don
If the case is grounded then the short circuit protection will operate. If the case is not grounded then the enclosure will be elevated to line voltage. The totsl circuit resistance will be the body's resistance, including shoewear, and the earth's resistance from the point where the person stands to the nearest connection of the grounding system to the earth.
The total voltage difference is spread along the line between the ground fault point and the earth bonding point of the grounded conductor.
See OSHA 1910.269
""Step potential" is the voltage between the feet of a person standing near an energized grounded object. It is equal to the difference in voltage, given by the voltage distribution curve, between two points at different distances from the "electrode". A person could be at risk of injury during a fault simply by standing near the grounding point."
So if the equipment is grounded there will be no voltage as the OC/SC protective device will open the circuit. If the equipment is not grounded the only time the person would be in danger if the power source AND it's grounded service wire bonding connection to the earth is closer than ~10' or if the person is grabbing a nearby grounded object with his other hand.
The curious can conduct a simple experiment: