If the sub-sub panel is correctly installed (no neutral to enclosure or EGC bond) the conduit and the EGC are not in parallel with the neutral and only carry current under fault conditions.If i run conduit from sub to main panel, the conduit and EGC would carry current and would be in parallel with the neutral.
IF you bonded the neutral and ground in the sub-panel, yes, which is why you shouldn't do it.If i run conduit from sub to main panel, the conduit and EGC would carry current and would be in parallel with the neutral.
YOU ARE WRIGHT THANK YOU !If the sub-sub panel is correctly installed (no neutral to enclosure or EGC bond) the conduit and the EGC are not in parallel with the neutral and only carry current under fault conditions.
so the only reason we don't bond the sub feed, is if we loose a neutral the sub box becomes energized ?IF you bonded the neutral and ground in the sub-panel, yes, which is why you shouldn't do it.
The hazard is metal surfaces expected to be at zero volts to earth suddenly becoming energized.
I wouldn't say "only" but it's a big one. Think about the old 3-wire major-appliance circuits.so the only reason we don't bond the sub feed, is if we loose a neutral the sub box becomes energized ?
What is the main reason for this ???????????????????????????????????????????????????????????????????I wouldn't say "only" but it's a big one. Think about the old 3-wire major-appliance circuits.
Or feeding a receptacle with one conductor for both grounded and grounding purposes.
I don't understand your question.What is the main reason for this ???????????????????????????????????????????????????????????????????
Why do we not bond the sub feed?I don't understand your question.
Then, yes, what we have explained and what you understood is the main reason.Why do we not bond the sub feed?
There are multiple reasons. If you lose the neutral stuff becomes energized, current flowing in raceways which raises the potential from ground,. Neutral current taking paths that it's not intended to, sparking between different paths with different resistances.....What is the main reason for this ???????????????????????????????????????????????????????????????????
If you lose the neutral at the main service, the conduit to the sub and the sub panel will become energized . with 4 wires or 3 wires ?Then, yes, what we have explained and what you understood is the main reason.
As I said, its why we don't use one wire for both a circuit conductor and grounding.
Your service does, but its established as the zero-volts reference for the premises.
Years ago, a customer's son was badly shocked because the neutral wire in the 3-wire range feed pulled out of the lug in the range's wiring compartment.
If you mean ahead of the service disconnect, which affects everything, a sub-panel wired either way could become energized. Earth alone is not conductive for made electrodes to prevent this.If you lose the neutral at the main service, the conduit to the sub and the sub panel will become energized . with 4 wires or 3 wires ?
If you lose the neutral at sub feed on a 4 wire , no problem .other than 120 volt things wont work?If you mean ahead of the service disconnect, which affects everything, a sub-panel wired either way could become energized. Earth alone is not conductive for made electrodes to prevent this.
If the neutral/grounding bond remains intact, there will still be little to no voltage between the neutral and the EGC, whether pipe or conduit. (If both, they should be bonded together everywhere.)
In a metal water-pipe neighborhood, such a break could remain undetected for some time. Otherwise, you get the bright and dim lights from the classic broken-neutral caused voltage imbalance.
Not exactly. Any difference in load current between the lines will cause the voltages to shift. Voltage on the neutral will rise from zero, causing some loads to receive too little voltage and others too much.If you lose the neutral at sub feed on a 4 wire , no problem .other than 120 volt things wont work?
If you lose the neutral at the main panel the main panel and the 3 wire sub the sub panel surface becomes energized . with 4 wire the sub panel surface will not become energized . if you lose the neutral at a 3 wire sub the surface will become energizedNot exactly. Any difference in load current between the lines will cause the voltages to shift. Voltage on the neutral will rise from zero, causing some loads to receive too little voltage and others too much.