By who? Was it the POCO, they may have a rule but it is not in the NEC.I was told from meter to panel it cant be over 8 ft
By who? Was it the POCO, they may have a rule but it is not in the NEC.I was told from meter to panel it cant be over 8 ft
Ask him where you can read it for yourself? I know some areas have a specified length for 230.70(A)(1) but the NEC does not.My 75 year Master electrician. I never seen it but that's what he says. I guess I will post that next.
If the conductors are on the outside of the structure then the NEC has no limit as to the length of the conductors. If the conductors are entering the structure then the section that Roger mentions in post #23 would apply but that has no specific limit either. Your master electrician needs to clarify where the 8' comes from.I was told from meter to panel it cant be over 8 ft
If the conductors are on the outside of the structure then the NEC has no limit as to the length of the conductors. If the conductors are entering the structure then the section that Roger mentions in post #23 would apply but that has no specific limit either. Your master electrician needs to clarify where the 8' comes from.
Well it's possible that someone has established 8' as the allowable limit in your area. Again the NEC doesn't say that it's 8'. It could just be what the AHJ has allowed to meet their definition of the word nearest so the master might be correct based on that.I am so confused now. he said from meter outside once it enters the house max 8 ft. maybe it is just alliant. Thanks
you run the wires through the sub panel which was the main panel before we started this process to the Generac t switch. sorry i am not very smart and i guess i cant read either. i just dont see where is says that.
Wondering if you could help me figure out if this is against code. I have an inspector who says it's a violations. He is not approving it but still would like to learn how it is a violation. I am not using panel as a Chase but I have Don about 10 that way since last post and everyone says it is legal.Actually there is no issue with using the panel as a chase, the issue is with having service conductors in the same raceway or cable. Fill might also be an issue in that nipple too as he was really struggling to get them all through.
Yes and conclude you can use it as a chase.Have you read 230.7?
Are unfused service conductors in the chase?Yes and conclude you can use it as a chase.
There are conductors from meter not breakeredAre unfused service conductors in the chase?
BingoThere are conductors from meter not breakered
I get it just wanted some clarification. Mike Holt says you can.Let me clarify, I see your argument but regardless of the illustration the inspector can interpret his way IMO.