- Location
- Southeast PA
I'm installing a subpanel into a single family dwelling finished basement. I have two choices for the location of a 100A subpanel, to the left of the main panel or below the main panel. There will be a wall built in front of the panels about 1 ft out. The wall will have double doors so when open the 3ft depth requirement will be satisfied for the main panel (The width of the doors will be 60"+ with nothing in between them). If the subpanel is installed immediately to the left of the main panel, the leftmost 3"-5" of the subpanel will only have 1ft of depth even with the doors open. Would this violate 110.26 or any other code if the subpanel door can still be opened 90deg and it's breakers have 3+ ft of clear space in front of them? Or could/should it be installed directly below the exisiting main panel (which is 55" from the floor to the bottom of the panel)?