jeff43222
- Minneapolis, Minnesota
I recently rewired a kitchen in a single-family dwelling, and today I went in to install a subpanel to accommodate all the new circuits. Unfortunately, I discovered that the existing main panel (100A, QO, 20 space, almost full) can only handle #8 wire on the neutral bar, but I was planning on putting in something bigger than that.
My concern is that a 50A breaker protecting the feeder to the subpanel might not be enough for the potential loads that might be encountered. Here is what I installed in the kitchen:
15A ckt for undercab Xenon lights (80 watts total)
15A/15A circuit for split-wired disposal/dishwasher recp
2 20A ckts for small appliances
1 20A ckt for the built-in microwave
1 30A ckt for the dual-fuel range
If it weren't for the range, I'd say 50 amps is plenty, but I was thinking that if all the circuits were pushing the envelope, it wouldn't be too surprising if the 50A breaker tripped. Homeowners said they do a lot of cooking/baking, and they use the usual countertop appliances (coffee machines, toasters, etc.).
I'd really prefer to give them an installation where they wouldn't have to think twice about running the coffee maker and the microwave at the same time the dishwasher and range are on, but the only way I can see that is if I swap out the main panel.
Anyone care to offer up an opinion?
[ August 24, 2005, 03:51 PM: Message edited by: jeff43222 ]