A 100 amp subpanel for an addition is wired with SE cable from the main panel to the 100 amp breaker in the subpanel. The subpanel neutral bar is isolated from the panel and grounded to a ground rod with #6 bare copper. Grounds are terminated on the neutral bar. I see several problems here:
(1)The feeder wire to the subpanel requires an insulated neutral.
(2) A grounding conductor is required from the main panel to the subpanel which must be in the same cable or raceway as the conductors.
(3) The neutrals and grounds should be separated with a grounding terminal bar.
I think the SE feeder cable should be replaced with either 4 conductor SER cable with or 4 individiual THHN insulated conductors in conduit to take care of items 1 & 2.
Two questions --
1) Am I on the right track with 1,2,and 3 above?
2) Is there any problem leaving the #6 bare ground connected from the subpanel grounding bar to a ground rod?
(1)The feeder wire to the subpanel requires an insulated neutral.
(2) A grounding conductor is required from the main panel to the subpanel which must be in the same cable or raceway as the conductors.
(3) The neutrals and grounds should be separated with a grounding terminal bar.
I think the SE feeder cable should be replaced with either 4 conductor SER cable with or 4 individiual THHN insulated conductors in conduit to take care of items 1 & 2.
Two questions --
1) Am I on the right track with 1,2,and 3 above?
2) Is there any problem leaving the #6 bare ground connected from the subpanel grounding bar to a ground rod?