Here is the situation: I have discovered (in my recently purchased home), the electrician ran ONE 12/2 UF cable from the main panel to the 2nd garage's subpanel. I estimate it's a 450 foot run. The cable was run in 1 inch poly irrigation pipe. I'm pretty sure it's not HDPE conduit as I saw no markings on the section I unearthed. The voltage drop calculators say I need to run 6 awg cable to get 20 amps at the subpanel with 3% voltage drop. Is it a code violation to run URD cable through that pipe?

Single conductor 6 awg URD cable is more expensive than 4-4-4-4 URD quadraplex cable, however it doesn't look like Appendix C in the 2017 NEC lists fill capacity for direct bury wire. Since URD likely has thicker insulation than THWN or XHHW I don't think I would be allowed 4 conductors at 4 awg, My assumptions are compact conductor wire will be used and the 1 inch poly pipe has equivalent diameter to 1 inch HDPE conduit.

The reason I'm going through this exercise... For new conduit I have to run it down my compacted gravel driveway, over my buried utility line, the buried 7200 volt service to the transformer that services my house and my neighbor, 3 drain culverts, underground natural gas service 2 or 3 times, and under a private dirt road to my garage.

I did check with my local electric co about running service to the garage. Their fees seemed reasonable but I'll pay $20 month for the 2nd meter. I have a whole house generator so I'd keep the current subpanel for lights and the garage door opener.
 
I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top