- Licensed Electrician
Wrong. Earth connection will not help you in clearing a fault.EARTH connection will NOT help you from getting a shock '
Agree in the context of all of the electrical world, at least the North American part of it.Earth connection will not help you from getting a shock either, unless one of the electrodes is a very low impedence path back to the source like a metal water pipe connected to another service. In that case, the lost neutral may not be noticed for years. But dirt will not lower the potential between the service with the lost neutral and ground any significant amount unless you are standing right on the electrode.
The post that winnie made holds true again in your question here. There is no direct yes or no answers, but the short answer is you are less likely to get shock at the service panel no matter what the condition of the neutral because the connection to earth is right there and you have the requirements for all the metal raceways to be connected with more than a simple lock nut.
Disagree in the context of the discussion at hand.
I am seeing the discussion having to do with why we don't re-bond the neutral at sub panels.Can you explain what you mean by " context of the discussion at hand", I'm a little confused, maybe we are talking about different things?
That naturally leads into questions about the service, where we have code mandated neutral current on metal parts. That's why we have rules about service raceways needing a bonding lock nut and the GEC being at the service.
If both the main and sub are bonded to neutral, their cabinets will be at different potential because of the voltage drop on the neutral conductor. Of course this will be very small and imperceptible during normal operation but in some rare circumstances could be a shock hazard, for example during a fault (high current flowing=how voltage drop).
Let's try it this way....Earth connection will not help you from getting a shock either, unless one of the electrodes is a very low impedence path back to the source like a metal water pipe connected to another service. In that case, the lost neutral may not be noticed for years. But dirt will not lower the potential between the service with the lost neutral and ground any significant amount unless you are standing right on the electrode.
Not likely unless the neutral and the conduit both are high resistance paths. The only voltage that is available to drive a shock is the voltage drop on the parallel path that consists of the neutral conductor and the conduit. If the wire is in a good condition, then there will be only a few volts, at most, to drive the shock.Yes, and along with that, you wouldn't have to lose a neutral to be shocked. Current will flow on both the neutral and any metal it is connected to. So if you touched the EMT and something else that is grounded it will shock you. That is if the neutral and ground were bonded again at the subpanel.
Why can't an open neutral at the service give you a shock? If you have an open neutral and a single 120 volt load the load end of the open neutral will be at 120 volts.Let's try it this way....
In the case of a line to earth fault anywhere in the system, yes you would have to be standing right on the ground rod to not get a shock but, an open neutral at the service I don't think you would get much of a shock at all. An open neutral at a sub-panel where the neutral is not isolated can give you a nasty shock.