curt swartz
Electrical Contractor - San Jose, CA
- Location
- San Jose, CA
- Occupation
- Electrical Contractor
I think you are missing the point. What if the feeder is not in a small house? It's not uncommon to have 100 amps of heating or cooling load in a larger dwelling. The feeder might be supplying pool equipment, hot tub or combination of loads that may be continuous.I think you are adding too much if factor to this. A small home would not require a very big air condtioner any any case so that load would be diversive also. You certainly arent going to have more than one ac unit on the panel anyway. I know what the code says but I dont agree that is necessarily logical when it comes to this specific area. Anyhow just use 2 al and a 90 amp breaker and you are good to go.