AB claims they are ul489
I think you are right. Listed to ul508 and not ul489.These are not molded case breakers listed under UL489 for branch circuit protection. There are designed to meet IEC motor protection requirements. As such the contain an amount of phase loss protection as part of the overload mechanism. This phase loss 'sensitivity' causes the device to trip somewhat early if there is a current imbalance.
The jumper makes sure that all of the phases see an equal amount of current therefore preventing the phase loss early trip.