I am in the process of installing some interior and exterior lighting, recepts and switching in a large detached building. About a third of the way through this process the owner mentioned that sometimes when the kids come in the from the pool with wet feet and touch the refrigerator they feel a "tingle".
What I found was the house has a 320 amp. undergound service with a 200 amp panel located inside the home. The service is grounded at the meter socket with rods, all plumbing in the house and the outbuilding is plastic. There is a 200 amp. disconnect on the exterior of the home which then feeds underground in 2" PVC about 50' to the outbuilding. The feed is 3-wire 3/o copper to a 200 amp. load center located inside the building. The grounded conductor and the EGC's are landed together on the neutral bar in the panel with no additional grounding present. I pulled the EGC on the refrigerator circuit and got 18 volts with the frig. running.
What I would like to do is pull an additional EGC from the main service, install rods, isolate neutrals and grounds at the building panel, however I don't think pulling the 4th conductor is going to be feasible with the owner.
Do I have any other options here that I am missing? This property is way out in the boonies, no permits or inspections. They don't even have zoning yet. If they even have an electrical code it's not the '08.
Most of my experience has been in new construction so we just did it right from the getgo. Should I be looking anywhere else for the source of this unwanted voltage? Pools, kids and electric scare the heck out of me since a 12 year old girl was electrocuted last summer about 30 minutes from where I live. Any assistance on options on this would be greatly appreciated on this end.
What I found was the house has a 320 amp. undergound service with a 200 amp panel located inside the home. The service is grounded at the meter socket with rods, all plumbing in the house and the outbuilding is plastic. There is a 200 amp. disconnect on the exterior of the home which then feeds underground in 2" PVC about 50' to the outbuilding. The feed is 3-wire 3/o copper to a 200 amp. load center located inside the building. The grounded conductor and the EGC's are landed together on the neutral bar in the panel with no additional grounding present. I pulled the EGC on the refrigerator circuit and got 18 volts with the frig. running.
What I would like to do is pull an additional EGC from the main service, install rods, isolate neutrals and grounds at the building panel, however I don't think pulling the 4th conductor is going to be feasible with the owner.
Do I have any other options here that I am missing? This property is way out in the boonies, no permits or inspections. They don't even have zoning yet. If they even have an electrical code it's not the '08.
Most of my experience has been in new construction so we just did it right from the getgo. Should I be looking anywhere else for the source of this unwanted voltage? Pools, kids and electric scare the heck out of me since a 12 year old girl was electrocuted last summer about 30 minutes from where I live. Any assistance on options on this would be greatly appreciated on this end.