charlie b said:What am I missing here?
Considering he is only reading 18 volts on a 120 volt appliance suggests a high resistance ground fault IMO.
charlie b said:What am I missing here?
gar said:080614-2141 EST
AWC:
Think this thru.
What are typical resistances thru the ground from one ground rod to another spaced maybe 50 ft apart? You can do some experiments to get an idea for your area (use 28 V AC). You can look at the specs in the NEC for maximum ground rod resistance and judge from this.
Now isolate the neutral and EGC at the subpanel and connect the neutral to a ground rod at the subpanel. This means there is no path for current into the subpanel EGC except thru earth back to the center tap of the supply transformer.
Now assume the ground resistance is 10 ohms. Thru a short circuit from a hot wire at the subpanel to the EGC you apply 120 V to the EGC. How much current flows in the EGC. What is the resistance of 50 ft of 000 copper wire? With the hot wire at the subpanel shorted to the EGC what is the voltage drop on the 000 wire due to the short, and in turn what is the voltage on the EGC wire assuming 120 V at the home main panel?
Doing this analysis may answer your question.
.
awc said:Ok, I think maybe i'm getting this but would the best way to have done this from the beginning been to have the fourth conductor for the EGC? Sorry for the delay but didn't get a chance to examine this until tonight. Would you want to treat it as a branch circuit? Sorry if you're ready to slap me but I just want to be straight on this. Thank you in advance for your help
ElectricianJeff said:I think this is starting to sink through this thick skull.
Jeff
quogueelectric said:I think you have a bad ground from the main panel to the fridge receptacle.
you could use a simple cube receptacle tester to check this. Many times the lighting circuits in a fridge go bad and get shorted to the metal of a fridge from sockets and or door switches rusting out.
The voltage is either coming up from the concrete and flowing to the grounded refridgerator door.
Or the refridgerator door is energized and flowing down to the concrete which is the more likely scenareo.
I have never seen a full sized fridge without a 3 prong plug and I would think the frame of the fridge would be grounded.
In your test with the gfci on the fridge you should have put a jumper wire from the door to the wet floor or something with a known good ground and seen if the gfci would trip.
Then you know the objectional current is coming from the fridge door and not the floor.
If the door became energized and it did not have a path to flow to the gfci experiment would not trip the device.