photonboy
- Berkeley, CA, USA
- Ex roof monkey, current desk jockey
I was under the impression that the sum of all breakers rule is another way of saying the 120% rule, which says the MB and PV breaker cannot exceed 120% of bus bar rating. One of our installers is pushing back on this. There is no PCS in this system, just a SolarEdge inverter with no PCS capabilities.
Scenario:
200A bus
200A Main Breaker
1 existing 30A load breaker
1 new 60A PV backfeed breaker
The installer is claiming that the "sum of all breakers rule" means that you just add up the sum of the breakers present on the bus, minus the Main Breaker, and if that is less than the bus rating then good to go.
Here are the pics they uploaded to make their point and my marked up response, which is correct?:
Scenario:
200A bus
200A Main Breaker