kwired
Electron manager
- Location
- NE Nebraska
For your typical self contained dwelling or light commercial smaller drainage or sewage lift stations I never seen one not cord and plug connected.And in many cases the 2017 requires sump pumps to be on a gfci. The code does not state sump pump per se, but it does state outlets installed in unfinished basements, etc must be gfci. Back then you could get by with a direct wired pump
@jmellc -- check to see if they make a direct wired sump pump. I am betting they don't make them.
BTW, NC is on the 2017
I have seen larger three phase submersible pumps that are not cord and plug connected pumping in a variety of situations from rainwater, to municipal lift station pumps to livestock manure pumps.
Does NEC define a sump pump or is there an actual listing for what is a sump pump vs what other submersibles are classified as?
A municipal lift station I used to do service work at occasionally had pumps submersed in the holding tank but were driven by long shafts coupled to motors located well above the holding tank. Basically performing same function but certainly did not have a submersible motor involved.
I think NEC went wrong way with this requirement. GFPE protection seems legitimate for such equipment. But then they also complicate it with GFCI protection necessary for receptacles in certain locations regardless the equipment it is intended to supply.