Regardless GFCI protection is required if the receptacle is in a location that requires GFCI protection. The protection is for the receptacle not the sump pump. For those in NJ the point is moot.
Agreed.
90.1 Purpose.
(B) Adequacy. This Code contains provisions that are considered
necessary for safety. Compliance therewith and
proper maintenance results in an installation that is essentially
free from hazard but not necessarily efficient, convenient,
or adequate for good service or future expansion of
electrical use.