Mustwin351:
I believe you paid no attention to what I wrote about troubleshooting.
It appears that terminals 6 and 7 are the start float, high level float, and you measured voltage to ground on all terminals except 7 (I have no idea what ground is --- however I assume it is your neutral or common wire, TB 1-3). What I suggested was that you short 6 and 7 and see if that caused the pump to run. If that short did not cause the motor to run, then the problem is in the controller. If the short caused motor run, then the problem is in the wiring to the float, and/or in the float.
A little more thought makes me think the problem is with the float or its wiring. In automatic the high level float should be supplied with power from your hot supply line. Since you read full voltage on terminal 6 this means power is going to the high limit float wiring, but since 7 reads 0 V it means the high limit float circuit is not closing when the float is supposed to be closed.
.
Ran out of time on addition to post. See added comment at bottom.
Mustwin351:
I believe you paid no attention to what I wrote about troubleshooting.
It appears that terminals 6 and 7 are the start float, high level float, and you measured voltage to ground on all terminals except 7 (I have no idea what ground is --- however I assume it is your neutral or common wire, TB 1-3). What I suggested was that you short 6 and 7 and see if that caused the pump to run. If that short did not cause the motor to run, then the problem is in the controller. If the short caused motor run, then the problem is in the wiring to the float, and/or in the float.
A little more thought makes me think the problem is with the float or its wiring. In automatic the high level float should be supplied with power from your hot supply line. Since you read full voltage on terminal 6 this means power is going to the high limit float wiring, but since 7 reads 0 V it means the high limit float circuit is not closing when the float is supposed to be closed.
.