True, but where would find a 120 volt sump pump that is suitable for anything other than cord and plug?No. And neither does a 240V pump.
Good point. It would not be legal to cut the cord cap off of a 120V sump pump just to avoid the GFCI requirement.True, but where would find a 120 volt sump pump that is suitable for anything other than cord and plug?
True, but where would find a 120 volt sump pump that is suitable for anything other than cord and plug?
True, but the sump pump is not what requires GFCI protection, it is the location of the 15/20 amp 120 volt receptacle that kicks in GFCI requirements. Just so happens those sump pumps are commonly in a location that will require a GFCI if you use a 15/20 amp 120 volt receptacle.
Such exceptions to rules went away with the 2005(I think) NEC and never came back, not just for sump pumps, but for any situation where GFCI is required yet there is permanent equipment that plugs into a 15/20 amp 120 volt receptacle.Isnt there a rule for a single outlet that is dedicated circuit for a sump pump exempting it from GFCI requirement?
Some areas have local amendments that allow the single outlet exemption.Isnt there a rule for a single outlet that is dedicated circuit for a sump pump exempting it from GFCI requirement?
Some areas have local amendments that allow the single outlet exemption.
Are you sure you want an exemption?
Mother-Daughter-Electrocuted-in-Flooded-Montgomery-Co-Basement
It's not clear if the sump pump was plugged into an outlet that was under water, the sump pump itself was under water or if they used an extension cord with the female end in the water.
Regardless of what the source of power was, if it was protected by a GFCI the water would not have become energized.
Are you sure you want an exemption?
Mother-Daughter-Electrocuted-in-Flooded-Montgomery-Co-Basement
It's not clear if the sump pump was plugged into an outlet that was under water, the sump pump itself was under water or if they used an extension cord with the female end in the water.
Regardless of what the source of power was, if it was protected by a GFCI the water would not have become energized.
I totally agree but I wish they would make or use condensate pumps that were direct wired. As it stands now it must be on a gfci if it is in a crawl space and it causes issues
What issues?
If for any reason that gfci trips, the ho isnt likely to know it. then again, ive never met a ho that did regular checks or maintenance on condensate pumps; we find them running continuously on a somewhat regular basis.