If sump pumps in the basement are connected to single receptacles is GFCI protection required? There happens to be 2 pumps.
I understand that the CMP's are looking to protect as many people as possible from dangerous situations but, if that clueless HO is wading through knee deep water in his basement, knowing there is live electric there, the lack of GFCI protection for the sump pump maybe the least of his problems. Like John Wayne once said "Life is tough but it's even tougher when you're stupid."I'm thinking of clueless HOs wading through knee deep stuff to a failed pump but the GFCI has not tripped, because there isn't one...not a good thought.
As far as the significant and the GD not working...she knows where the walk in doors are and she won't melt because of a little rain.
I was always under the impression that a single receptacle fpr a sump pump mounted high enough where it wasn't "readily accessible" wasn't required to be GFCI protected but I think that's changed. Maybe it's in the 2020 Code but I vaguely remember being told that in a CEU class.Here in NJ GFCI protection is not required for a single receptacle serving a sump pump.
Almost every receptacle in an unfinished basement has required GFCI protection since the 2008 NEC. There is no accessibility rule attached to that requirement. NJ has kept the pre-2008 exceptions which permit a single receptacle for a sump pump in a location that would normally require GFCI protection.I was always under the impression that a single receptacle fpr a sump pump mounted high enough where it wasn't "readily accessible" wasn't required to be GFCI protected but I think that's changed. Maybe it's in the 2020 Code but I vaguely remember being told that in a CEU class.
He never said she was fine with that, just that she knew where the door was and that she wouldn't melt in the rain.I understand that the CMP's are looking to protect as many people as possible from dangerous situations but, if that clueless HO is wading through knee deep water in his basement, knowing there is live electric there, the lack of GFCI protection for the sump pump maybe the least of his problems. Like John Wayne once said "Life is tough but it's even tougher when you're stupid."
Doesn't sound liker you married the same woman the rest of us did.
IIRC all receptacles in basements (at least in dwellings) require GFCI protection in 2020 NEC, they basically removed "unfinished" from the wording.I was always under the impression that a single receptacle fpr a sump pump mounted high enough where it wasn't "readily accessible" wasn't required to be GFCI protected but I think that's changed. Maybe it's in the 2020 Code but I vaguely remember being told that in a CEU class.
It is not often that the members of the CMPs write code rules.....in most case the rules originate with a Public Input and the panel members vote on the PI and issue a panel statement explaining their thoughts on the PI.This is one of those Code requirements that makes you scratch your head and wonder what the CMP's were thinking when they wrote it. ....
Yes you need to follow both but electricians don't install sump pumps they install the receptacle. Here is NJ if you install a single receptacle it would be code compliant. If someone plugs in a sump pump that requires GFCI protection according to the instructions that's not the electricians responsibility.My boss told me to always follow the code. and the instruction manual
That's the whole point IMHO. If it's only one or two people who weren't careful or didn't know what they were doing, why write a Code section to affect the entire industry ?I would love to see some data that stated how many people have been hurt by unplugging the sump pump and using that single receptacle for something else. My guess is that it's near zero.
OK. I can buy into that line of thinking. But, the members of the public are not the ones writing the Code section - it's the CMP's. So now, if one (public) person gets shocked while pulling out a sump pump cord, does that justify writing a Code section requiring ALL sump pumps to have GFCI protection ?It is not often that the members of the CMPs write code rules.....in most case the rules originate with a Public Input and the panel members vote on the PI and issue a panel statement explaining their thoughts on the PI.
This is similar to the GFCI protection requirement for AC units.OK. I can buy into that line of thinking. But, the members of the public are not the ones writing the Code section - it's the CMP's. So now, if one (public) person gets shocked while pulling out a sump pump cord, does that justify writing a Code section requiring ALL sump pumps to have GFCI protection ?