Since a receptacle feeding a sump pump in an unfinished basement requires GFCI protection, I’ve seen most contractors in the area using a duplex 15 amp GFCI to satisfy the requirement.
I believe the code considers this a multi-outlet branch circuit, and I’m wondering if this may be a violation of 210.23a2 depending on the size of the pump involved.
For instance, if we have a 1/2 HP 120 volt sump, Table 430.248 puts the FLC at 9.8 amps- over 50% of a 15 amp circuit.
I don’t know how common a 120 volt sump over 1/2hp is but it looks like anything larger than that puts us beyond 50% of a 20 amp circuit. Are single GFCI receps or standard single receps and GFCI breakers required in these cases?
Is my thinking off on this?